[UL-83] Section 41 VW-1 Flame Test 관련

페이지 정보

작성자 현대EDS 작성일17-03-17 15:19 조회22,402회 댓글0건

본문

[Wire] Thermoplastic-insulated Wire, ZLGR

 

[자료출처: UL Product Spec. ]

[의견] UL VW-1 Flame Test는 UL1581 Section 1080을 따른다. 이는 455mm 시료, 500W Flame (Bunsen Burner), 시료위치는 Vertical, 불꽃위치는 20​o​, 1분 이상 견디어야 하며, 시료 아래에 놓여 있는 솜을 점화시키지 않아야 한다. 

USE

This category covers thermoplastic-insulated wire for use in accordance with Article 310 of ANSI/NFPA 70, "National Electrical Code."

PRODUCT TYPES

Thermoplastic-insulated wire is rated 600 V and is designated as follows:

TW — Indicates a single conductor having flame-retardant, moisture-resistant thermoplastic insulation. The wire is rated 60°C wet or dry.

THHN — Indicates a single conductor having flame-retardant and heat-resistant thermoplastic insulation with a jacket of extruded nylon or equivalent material. The wire is rated 90°C dry only.

THW — Indicates a single conductor having flame-retardant, moisture- and heat-resistant thermoplastic insulation. The wire is rated 75°C wet or dry.

THW-2 — Same as THW except that the wire is rated 90°C wet or dry.

THHW — Indicates a single conductor having flame-retardant, moisture- and heat-resistant thermoplastic insulation. The wire is rated 90°C dry and 75°C wet.

THWN — Indicates a single conductor having flame-retardant, moisture- and heat-resistant thermoplastic insulation with a jacket of extruded nylon or equivalent material. The wire is rated 75°C wet or dry.

THWN-2 — Same as THWN except that the wire is rated 90°C wet or dry.

FEP — Indicates a single copper conductor having flame-retardant and heat-resistant thermoplastic (fluorinated ethylene propylene) insulation. Type FEP wire is suitable for use at 90°C and lower temperatures in dry locations. It is also suitable for use in dry locations at 200°C and lower temperatures for special applications.

FEPB — Indicates a single copper conductor having flame-retardant and heat-resistant thermoplastic (fluorinated ethylene propylene) insulation with a glass braid. Type FEPB wire is suitable for general use at 90°C and lower temperatures in dry locations. It is also suitable for use in dry locations at 200°C and lower temperatures for special applications.

PFA — Indicates a single copper conductor having flame-retardant and heat-resistant thermoplastic (perfluoroalkoxy) insulation. Type PFA wire is suitable for use at 90°C and lower temperatures in dry locations. It is also suitable for use in dry locations at 200°C and lower for special applications.

PFAH — Indicates a single, nickel or nickel-coated copper conductor having flame-retardant and heat-resistant thermoplastic (perfluoroalkoxy) insulation. The PFAH is suitable for use at 250°C and lower temperatures only for leads within apparatus or within raceways connected to apparatus, in dry locations only.

TFE — Indicates a single, nickel-coated copper or nickel base alloy conductor having flame-retardant and heat-resistant thermoplastic (polytetrafluoroethylene) insulation. Type TFE wire is suitable for use at 250°C and lower temperatures in dry locations as leads within apparatus or within raceways connected to apparatus or as open wiring.

Z — Indicates a single copper conductor having flame-retardant and heat-resistant thermoplastic (ethylene tetrafluoroethylene) insulation. Type Z wire is suitable for use at 90°C and lower temperatures in dry locations. It is also suitable for use in dry locations at 150°C and lower temperatures for special applications.

ZW — Indicates a single copper conductor having flame-retardant and heat-resistant thermoplastic (ethylene tetrafluoroethylene) insulation. Type ZW wire is suitable for use in dry locations at 90°C or wet locations at 75°C. It is also suitable for use in dry locations at 150°C and lower temperatures for special applications.

ZW-2 — Same as ZW except that the wire is rated 90°C wet or dry.

TBS — Indicates a single conductor switchboard wire having thermoplastic insulation and a flame-retardant nonmetallic covering. Type TBS is suitable for use at 90°C and lower temperatures in dry locations.

PRODUCT MARKINGS

Types TW, THW, THW-2, THHN, THHW, THWN, THWN-2, PFA, PFAH and Z in sizes 4 to 1 AWG for grounding conductors only and in sizes 1/0 AWG and larger for circuit and grounding conductors that are marked "Cable Tray Use" or "CT" comply with a vertical-tray cable flame test. Wire so marked may additionally be marked "Sunlight Resistant" indicating compliance with an artificial weathering test.

All types in all sizes that are marked "Sunlight Resistant" comply with an artificial weathering test.

Wire suitable for exposure to mineral oil is marked "Oil Resistant I" for 60°C oil resistance, or "Oil Resistant II" for 75°C oil resistance, on the surface of the wire. An Oil Resistant marking, by itself, does not include resistance to gasoline or similar light petroleum solvents.

Wire suitable for exposure to mineral oil and to liquid gasoline and gasoline vapors at ordinary ambient temperature is marked "Gasoline and Oil Resistant I" if suitable for exposure to mineral oil at 60°C, or "Gasoline and Oil Resistant II" if the compound is suitable for exposure to mineral oil at 75°C. Gasoline-resistant wire has been tested at 23°C when immersed in gasoline. It is considered inherently resistant to gasoline vapors within the limits of the temperature rating.

Wire that complies with a special vertical flame test is surface marked "VW-1."

Constructions in this category that comply with a flame and smoke test (as described in UL 1685, "Vertical-Tray Fire-Propagation and Smoke-Release Test for Electrical and Optical-Fiber Cables") may have the additional marking "ST1" indicating "Limited Smoke." (Note: The suffix "-LS," added to the Type letters, has also been used to indicate Limited Smoke. Effective November 15, 2004, only "ST1" may be used.)

In place of three of the markings described above, the following multinational markings may be used:

"SR" in place of "Sunlight Resistant"
"PR" in place of "Oil Resistant"
"GR" in place of "Gasoline and Oil Resistant"

Submersible Pump Cable — Indicates multiconductor cable consisting of two or three flat or two to six twisted insulated conductors with or without an overall jacket. The cable is labeled in size 14 AWG to 500 kcmil copper, and 12 AWG to 500 kcmil aluminum or copper-clad aluminum. The cable is tag marked "For Wiring Only Between Equipment Located at Water Well Heads and Motors of Installed Deep-Well Submersible Water Pumps." The insulation is surface marked "Submersible Pump Cable." The cable has not been investigated for direct burial in the earth.

Wire, in sizes mentioned below, may employ copper or aluminum, or copper-clad aluminum conductors. Wire with copper-clad aluminum conductors is surface printed "AL (CU-CLAD)" or "Cu-Clad Al." Wire with aluminum conductors is surface printed "AL."

Wire and cable employing compact-stranded copper conductors is so identified directly following the conductor size, wherever it appears (surface, tag, carton or reel), by "compact copper." The abbreviations "CMPCT" and "CU" may be used for compact and copper, respectively.

Tags, reels and cartons for product employing compact-stranded copper conductors have the marking: "Terminate with connectors identified for use with compact-stranded copper conductors."

SIZE AND CONDUCTOR INFORMATION

Types TW, THW and THW-2 are certified in sizes 14 AWG to 2000 kcmil copper and 12 AWG to 2000 kcmil aluminum or copper-clad aluminum.

Types THHN, THWN, THWN-2 and THHW are certified in sizes 14 AWG to 1000 kcmil copper and 12 AWG to 1000 kcmil aluminum or copper-clad aluminum.

Types TA, TBS, PFA, PFAH and Z are certified in sizes 14 to 4/0 AWG copper and 12 to 4/0 AWG aluminum or copper-clad aluminum.

Types ZW, ZW-2, FEP and FEPB are certified in sizes 14 to 2 AWG copper and 12 to 2 AWG aluminum or copper-clad aluminum.

PRODUCT IDENTITY

One of the following product identities appears on the product: 

    Insulated Aluminum Wire(for thermoplastic-insulated wire that contains aluminum conductors)

    Insulated Wire(for thermoplastic-insulated wire that contains copper or copper-clad aluminum conductors) 

ADDITIONAL INFORMATION

For conductor termination information, see Electrical Equipment for Use in Ordinary Locations (AALZ).

REQUIREMENTS

The basic standard used to investigate products in this category is ANSI/UL 83, "Thermoplastic-insulated Wires and Cables."

Wire using insulation containing a fluoropolymer is additionally investigated to ANSI/UL 83A, "Fluoropolymer Insulated Wire."

UL MARK

The Certification Mark of UL on the attached tag, reel, or on the smallest unit container in which the product is packaged, with or without the UL symbol on the product, is the only method provided by UL to identify products manufactured under its Certification and Follow-Up Service. The Certification Mark for these products includes the UL symbol, the words "CERTIFIED" and "SAFETY," the geographic identifier(s), and a file number.

Alternate UL Mark

The Listing Mark of UL on the attached tag, the reel, or the smallest unit container in which the product is packaged, with or without the UL symbol on the product, is the only method provided by UL to identify products manufactured under its Listing and Follow-Up Service. The Listing Mark for these products includes the UL symbol (as illustrated in the Introduction of this Directory) together with the word "LISTED," a control number, and the product name as appropriate: Thermoplastic-insulated wire that contains copper or copper-clad aluminum conductors has the product name "Insulated Wire"; thermoplastic-insulated wire that contains aluminum conductors has the product name "Insulated Aluminum Wire."

* * * * * * * * * * * * * * * * * * * * * * * * *

UL, in performing its functions in accordance with its objectives, does not assume or undertake to discharge any responsibility of the manufacturer or any other party. UL shall not incur any obligation or liability for any loss, expense or damages, including incidental or consequential damages, arising out of or in connection with the use, interpretation of, or reliance upon this Guide Information.

Last Updated on 2016-02-12

The appearance of a company's name or product in this database does not in itself assure that products so identified have been manufactured under UL's Follow-Up Service. Only those products bearing the UL Mark should be considered to be Certified and covered under UL's Follow-Up Service. Always look for the Mark on the product.

UL permits the reproduction of the material contained in the Online Certification Directory subject to the following conditions: 1. The Guide Information, Assemblies, Constructions, Designs, Systems, and/or Certifications (files) must be presented in their entirety and in a non-misleading manner, without any manipulation of the data (or drawings). 2. The statement "Reprinted from the Online Certifications Directory with permission from UL" must appear adjacent to the extracted material. In addition, the reprinted material must include a copyright notice in the following format: "© 2017 UL LLC". 